$A$ small town with a demand of $800 \; kW$ of electric power at $220 \; V$ is situated $15 \; km$ away from an electric plant generating power at $440 \; V$. The resistance of the two-wire line carrying power is $0.5 \; \Omega/km$. The town gets power from the line through a $4000-220 \; V$ step-down transformer at a sub-station in the town.
$(a)$ Estimate the line power loss in the form of heat.
$(b)$ How much power must the plant supply,assuming there is negligible power loss due to leakage?
$(c)$ Characterise the step-up transformer at the plant.

Vedclass pdf generator app on play store
Vedclass iOS app on app store
(N/A) Total electric power required,$P = 800 \; kW = 800 \times 10^3 \; W$.
Supply voltage at the town,$V = 220 \; V$.
Voltage at which the electric plant generates power,$V' = 440 \; V$.
Distance between the town and the power generating station,$d = 15 \; km$.
Resistance of the two-wire line $= 0.5 \; \Omega/km$.
Total resistance of the wires,$R = (15 + 15) \times 0.5 = 15 \; \Omega$.
$A$ step-down transformer of rating $4000-220 \; V$ is used in the sub-station.
Input voltage to the transformer,$V_1 = 4000 \; V$.
The current in the transmission line is $I = \frac{P}{V_1} = \frac{800 \times 10^3}{4000} = 200 \; A$.
$(a)$ Line power loss $= I^2 R = (200)^2 \times 15 = 40000 \times 15 = 600,000 \; W = 600 \; kW$.
$(b)$ Total power supplied by the plant $= \text{Power required} + \text{Power loss} = 800 \; kW + 600 \; kW = 1400 \; kW$.
$(c)$ Voltage drop in the power line $= I \times R = 200 \times 15 = 3000 \; V$.
Total voltage transmitted from the plant $= \text{Voltage at transformer input} + \text{Voltage drop} = 4000 \; V + 3000 \; V = 7000 \; V$.
Since the plant generates at $440 \; V$,the step-up transformer rating is $440 \; V - 7000 \; V$.

Explore More

Similar Questions

How much current is drawn by the primary coil of a transformer,which steps down $220 V$ to $55 V$ to operate a device with an impedance of $275 \Omega$ (in $A$)?

In a step-up transformer,the turn ratio is $8:1$. $A$ $60\,Hz, 120\,V$ input is connected to its primary coil. The load resistance in the secondary coil is $10^4\,\Omega$. Find the current in the secondary coil.

The ratio of secondary to primary turns in a transformer is $3 : 2$. If the power output is $P$,then the input power,neglecting all losses,must be equal to:

$A$ current of $6 A$ is flowing at $220 V$ in the primary coil of a transformer. If the voltage produced in the secondary coil is $1100 V$ and $40 \%$ of power is lost, then the current in the secondary coil will be: (in $A$)

$A$ step-down transformer has $50$ turns on the secondary and $1000$ turns on the primary winding. If the transformer is connected to a $220 \ V, 1 \ A$ $A$.$C$. source,what is the output current of the transformer?

Vedclass Products

For Students

Vedclass Test Series

Mock tests in real JEE/NEET style with performance analysis. 5-day free trial.

Start Free Trial
For Teachers

Exam Paper Generator

Generate Set A/B/C/D exam papers from 7.5L+ questions in 2 minutes. 3 chapters free.

Try Free
For Institutes

Online Exam Module

Live online exams with unlimited students, 360° analytics & white-label branding.

See Demo